The calculated load of a service feeder has been calculated at 125 A and will be wired with a #1 AWG copper conductor at 75 degrees termination temperature. What is the maximum rating of overcurrent device permitted?
  1. 100 A
  2. 125 A
  3. 150 A
  4. 200 A
Explanation
Answer: C. Explanation: Table 2 states that the ampacity of #1 AWG copper is 130 A and Table 13 lists 150 A as acceptable overcurrent protection for wire of that ampacity. A 125 A overcurrent device would be permitted as it is less than the ampacity of the wire, but it is not the maximum permitted overcurrent device.